Transformer rating: 250 kVA
Primary voltage (high voltage side): 20,000 V (20 kV)
Secondary voltage (low voltage side): 400 V
Cooling type: ONAN (oil natural air natural), which is a common cooling system for transformers
Frequency: 50 Hz
Server specs: 220 V, 3500 W per server
Step 1: Calculate the total current capacity of the transformer on the low voltage side (400V):
The power rating of the transformer is 250 kVA, which corresponds to 250,000 VA. The current on the low voltage side (secondary side) can be calculated using the formula:
I=SV
I=VS
Where:
II = current in amps
SS = apparent power in VA (250,000 VA)
VV = voltage on the secondary side (400 V)
I=250,000400=625 amps
I=400250,000=625amps
So, the transformer can deliver 625 amps on the secondary side at 400V.
Step 2: Calculate the number of servers you can run per phase:
Each cryptocurrency server consumes 3500 W, and you want to know how many servers can be run per phase. Since you’re operating in a 3-phase system, we’ll distribute the load equally among the three phases.
The formula for the current draw on each phase is:
Iphase=PVphase×3×PF
Iphase=Vphase×3
×PFP
Where:
PP = Power in watts (3500 W per server)
VphaseVphase = Voltage per phase (220 V)
PFPF = Power factor (usually 1 for resistive loads like servers)
For 3500 W of load:
Iphase=3500220×3×1=3500381.8≈9.17 amps per server
Iphase=220×3
×13500=381.83500≈9.17amps per server
Step 3: Calculate how many servers each phase can handle:
Each phase can handle up to 6253=208.33 amps3625=208.33amps.
Now, we can calculate how many servers can fit in each phase:
Number of servers per phase=208.339.17≈22.7 servers
Number of servers per phase=9.17208.33≈22.7servers
So, each phase can handle 22 servers (since we can’t run a fraction of a server).
Step 4: Total number of servers:
Since there are 3 phases, the total number of servers you can run is:
Total number of servers=22 servers/phase×3 phases=66 servers
Total number of servers=22servers/phase×3phases=66servers